1/15/2022 3:52 PM | |
Joined: 1/15/2022 Last visit: 1/15/2022 Posts: 1 Rating:
|
I need to connect PAC2200 with Carel Boss via Modbus , whether anyone has a PAC2200 device configuration for Carel Boss? |
1/15/2022 4:23 PM | |
Joined: 9/27/2006 Last visit: 9/16/2025 Posts: 12409 Rating:
|
Hello mortenx; I have not worked with Carel Boss controllers, but their website states that they support both Modbus TCP and Modbus RTU connections. The Sentron PAC2200 offers both formats of Modbus also, which have you chosen for this project? The video link below shows how to use Siemens TIA Portal software (for a S7-1200 controller) to connect to a PAC2200 over Modbus TCP, if that can help you with the setup of the SENTRON unit side. To configure the PAC2200 for Modbu communications you need the powerconfig editor: - Parameterizing PAC2200 with SENTRON powerconfig https://support.industry.siemens.com/cs/ww/en/view/109746835/146457625099 - Download of Powerconfig software v3.19 https://support.industry.siemens.com/cs/ww/en/view/63452759 And in the SENTRON PAC2200 manual you will find a list of available registers, with ther Modbus offsets: - PAC2200 Modbus measured variables with the function codes 0x03 and 0x04 https://support.industry.siemens.com/cs/ww/en/view/109746835/146507142411 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 01/15/2022 16:25:03 |
|