10/30/2024 4:07 PM | |
Joined: 10/18/2007 Last visit: 9/16/2025 Posts: 82 Rating:
|
Hello all, We recently experienced an odd occurrence where a 410-5H system with latest FW and PCS7 V9.1 SP2 UC05 caused a self memory reset on the CPU without user prompt. I am curious to see if anyone has experienced something similar or has any clues as to what maybe going on. The PLCs were initially placed into STOP via the ES due to another issue and left in that state. About one week afterwards, the facility experienced a power outage that lasted 3 hours. This caused the PLCs, switches, PCs, and generally all associated PCS7 hardware to hard fault. After the 3hours, the power came back, all PCs and PLCs and balance of equipment energized concurrently. The PLCs at this point had both SYNC LEDs lit, and generating a sync error. Upon review of the CPU logs, post power outage, we found that the PLCs initiated a memory reset on themselves and fully cleared. This was without any user request or interaction. The PLCs naturally have flash based memory with new fully charged batteries. We would not have expected something like this, and personally I have never seen this in the countless times I have previously power cycled 410 controllers. Any and all ideas are welcome. Update: After further digging I found a thread that seems almost identical to the issue we had: S7 400 memory reset automatically - 166658 - Industry Support Siemens Does anyone know why a PLC will memory reset on sync module failure, and if there is anyway to avoid this as its extremely damaging to a running plant. BTW, in our case our modules were not failed UPDATE: (but I did replace the fiber optic cable from a 3rd party one to the official Siemens 410 sync cable, which resolved the SYNC error). Thank you! |
Last edited by: vadrad at: 10/30/2024 17:03:58Last edited by: vadrad at: 10/31/2024 14:43:58 |
|
10/30/2024 7:07 PM | |
Joined: 3/14/2008 Last visit: 9/16/2025 Posts: 2216 Rating:
|
Hi, The CPU410 can initiate memory resets on it's own. Even in some case when there is a battery backup already in place. Problems with synchronization cables can initiate a memory reset as well for example if both synchronization cables fail. Another case is if the CPU enters the DEFECTIVE state and if the problem is not solved, this will lead to an automatic memory reset. This is shown in the log (Memory reset started automatically). Do you have any logfiles saved from the CPU(s)? Maybe some additional info is logged... |
If I could help you, you can use the RATE button. Thank you. |
|
10/30/2024 7:24 PM | |
Joined: 3/14/2008 Last visit: 9/16/2025 Posts: 2216 Rating:
|
Hi, No problem! You can find the manual here: SIMATIC PCS 7 Process Control System CPU 410 Process Automation V8 |
Last edited by: Moderator_Lan at: 10/30/2024 22:22:44link optimized If I could help you, you can use the RATE button. Thank you. |
|
10/31/2024 8:02 AM | |
Joined: 3/14/2008 Last visit: 9/16/2025 Posts: 2216 Rating:
|
Hi, One thing to add. Have you take a look at the firmware list for the CPU410-5H? I suggest you update to the latest firmware because there are quite a lot of issues solved, for example:
and absolutely the problem that wins over all other problems
Remember, all above problems are fixed and therefore I suggest to update to the latest firmware |
If I could help you, you can use the RATE button. Thank you. |
|
10/31/2024 2:39 PM | |
Joined: 10/18/2007 Last visit: 9/16/2025 Posts: 82 Rating:
|
Hi Oreca,
Also please note that we are at firmware v8.2.4, and to my knowledge this is the latest rev. That being said, I recently spoke with support and was advised that new CPU firmware is expected in the next 2-3 months. It won't address this specific issue, but just giving a heads-up that an update is coming. Furthermore, I think based on your direction and piecing everything together, I have the following sequence of events mapped out: 1. The PLC started after a power loss with a SYNC error, and this is to my knowledge when a memory reset occurred within 60 seconds of them powering up. 2. I failed to mention, or make the connection till now, that the PLCs fiber sync cable was not the official Siemens cable supplied with the 410, but a 3rd party cable that a system integrator had lying around from other projects. I had the cable replaced with the Siemens cable and this immediately resolved the SYNC error (maybe coincidence, or maybe root cause). 3. At this point the PLCs were already reset, and until I recently reviewed the 410 system manual, I didn't realize that a SYNC error on startup will automatically force an internal memory reset on these PLCs. Based on the above, I feel this is likely what happened, but any additional input is certainly appreciated. Thanks again! AttachmentDiagnoseCPU0_19AUG2024.txt (177 Downloads) |
Last edited by: vadrad at: 10/31/2024 15:09:47Last edited by: vadrad at: 10/31/2024 15:11:06 |
|
11/1/2024 5:35 AM | |
Joined: 3/14/2008 Last visit: 9/16/2025 Posts: 2216 Rating:
|
Hi, I found two events in where the memory reset was executed automatically. Both during link up mode.See attachment. On that day (August 14) a lot happened, multiple attempts to put the AS system back in redundant mode and failed due synchronization errors. Good to you already replaced those synchronization cables with Siemens and I hope the problem is solved now. |