7/7/2013 10:41 AM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Dearygus, As you replaced 3 panels for the same reason in last 3 years, I do recommed to send the three panels to Siemens for inspection and repair. You can contact your local Siemens Office for this. As you know that profibus have +24VDC, 0 VDC in two pins of its bus connector. And in many cases, if there are fault (line to ground fault for example, and if the GND is connected to 0VDC), it will damage the communication partners connected to this network. Please tell us if there are any other nodes deffected on this profibus network? Are the 3 panels connected to the same network? What's type of power supply that fed the CPU and Panels? Do you have only one PS? I mean Does field devices fed from same PLC PS? Do you connected Earth of PS to clean earth system?
|
Last edited by: Ayman Elotaify at: 7/7/2013 10:47 AMAyman Elotaify |
|
10/19/2015 5:19 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4760 Rating:
|
New question published by Anup 1984 is split to a separate thread with the subject CPU315 & PP17 through profinet, can't see signals. Best regards |
3/13/2025 11:20 AM | |
Joined: 8/3/2009 Last visit: 9/12/2025 Posts: 16409 Rating:
|
Hello lingyunduobu you will not find probably a 1:1 replacement for the PP17 but you could use something link this (but its PN): https://mall.industry.siemens.com/mall/en/de/Catalog/Products/10087236 Also you should be considering updating also your PLC to a more modern one with ethernet. Bye Murof |
If this Information really helps, you could use the Rate function |
|
Follow us on