Hi AutoGen_4020818, The PLCSIM integrated in TIA Portal cannot communicate with any external device. If you are looking for that you need to use PLCSIM Advanced: |
If this Information really helps, you could use the Rate function |
|
1/27/2023 3:46 PM | |
Joined: 7/19/2022 Last visit: 9/15/2025 Posts: 436 Rating:
|
Oh, I'm sorry. The S7-1200 range CPUs cannot be used with PLCSIM Advanced as you can see in this manual: SIMATIC S7-PLCSIM Advanced V5.0. Supported CPUs S7-1200s can only be simulated with PLCSIM (How do you start S7-PLCSIM in STEP 7 (TIA Portal)?) and therefore cannot simulate communication with an external device.
|
If this Information really helps, you could use the Rate function |
|
1/27/2023 4:29 PM | |
Posts: 4 Rating:
|
Okei thank you its going to be the next thing i try |
1/27/2023 9:01 PM | |
Joined: 7/19/2022 Last visit: 9/15/2025 Posts: 436 Rating:
|
Check the following settings. In the panel: -Check that the transfer mode of the panel it's automatic. -Check the transfer protocol and the IP of the panel it's in the same subnet of the PC. In the en engineering PC: -Cehck that the IP of your PC it's in the same subnet of the panel. Try to perform a ping. -Check the PG/PC settings. Select your network adapter with the protocol TCPIP.1. -In the advanced load menu select the same protocolo that you selected in the panel (Ethernet or PN). Check the FAQ "Why can you not transfer the HMI configuration to the panel?" (https://support.industry.siemens.com/cs/ww/en/view/88633853). |