5/9/2018 6:14 AM | |
Joined: 4/23/2010 Last visit: 11/14/2024 Posts: 8092 Rating: (878) |
Hello, P575 is BICO parameter for selecting binector for tripping in case external fault signal is to be read, it is control word bit 15. So check the parameter back up to know the source of P575 binector or see r550 status on display if control word bit 15 is low or high. For details please refer attached sheet. AttachmentSimovert r550 status display.pdf (760 Downloads) |
This contribution was helpful to2 thankful Users |