Hello JEYAPRAKASH SP, The main point is, how you ensured that the drive/control card is having valid data? Unless & until it is confirmed, there is no point to proceed ahead. Please provide enable signals & reference voltage externally, power ON drive & check if it works or gives error. If it works, you need to check CNC side. If not you need to restore drive data correctly. One more point - where did you see F-07 fault? |
9/1/2022 8:39 PM | |
Joined: 10/17/2007 Last visit: 9/15/2025 Posts: 4452 Rating:
|
Finally you response. Believe me or not--I have been working with SIMODRIVE 611A the 1st day when Siemens release it (or earlier) . In 1990 , i had worked in the Siemens factory for this drive system near Nuremberg , Germany as final inspector. Now I need your machine / system story --is it used machine you just got it. and you are making set up to bring it into normal state? Or it was a running machine and something happened--made your 611A like what you said. also I want to see the picture of you E/R module status when you think it is ready --please post E/R module picture close look with 6 led's and better terminal block PS: safety remove the DC 600V cover most important the position from E/R module to the 1st drive (LT) module--I don't want you make low level mistake --DC bar not connected to drive. Response--I am sure will help you I think I attached manual for , but here is troubleshooting page AttachmentFEED_tb-shooting_fault_7.pdf (503 Downloads) |