Dear h2_504, HART is only allowed in decentral modules, because it's a fieldbus protocol.
You can use the module also central, but not with HART. The address-area of failsafe-modules seem to have more I/Os as expected, but not all of the area can be accessed. Some bytes are reserved for the ProfiSafe-protocol. Best regards, yy1 |
2/1/2012 10:15 AM | |
Joined: 11/8/2011 Last visit: 4/30/2025 Posts: 92 Rating:
|
Hi yy1! Thanks for the info. It was very useful. Best regards, h2_504
|