5/25/2023 9:18 PM | |
Joined: 10/30/2022 Last visit: 4/15/2025 Posts: 16 Rating:
Dear fellow PCS7 users, I came across your topic and decided to post another question in it as I am facing a similar problem. I have a number of 3WL circuit breakers in an MCC cabinet connected to a Sentron PAC meter through Modbus over RS-485. I can see all the devices downstream from the PAC meter but the connection is unstable and breaks down often. I am trying to decrease the baud rate of the PAC meter and the 3WL circuit breakers to see if that will fix the issue. However, I cannot change the modbus settings on he circuit breakers. The part number of the 3WL Modbus communication module is: 3WL9111-1AT15-0AA0 Does anybody know how to set up this module? Regards, Datigo Turia ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/26/2023 07:29:59New subject after splitting |
5/27/2023 3:29 PM | |
Joined: 3/28/2010 Last visit: 9/12/2025 Posts: 1172 Rating:
1. Baud Rate They recommend grounding the 3rd wire reference line at one end only, which in practice can be impossible because many Modbus RTU (RS-485) devices either do not provide a 3rd wire connection or their 3rd wire connection is grounded to the device itself. Siemens infers that the 3rd on this comm module, but it connects to other devices on the bus, so the ground potential of the other devices comes into play. Attachment92399994174_201908201154493814.pdf (792 Downloads) |
Last edited by: danw at: 05/27/2023 15:29:42Last edited by: Jen_Moderator at: 05/30/2023 05:29:47PDF attached from link. |