5/30/2022 3:19 PM | |
Joined: 6/3/2020 Last visit: 8/15/2025 Posts: 17 Rating:
Controller configuration in Xworks. |
5/30/2022 6:58 PM | |
Joined: 11/8/2017 Last visit: 9/15/2025 Posts: 356 Rating:
Hi, You don't necessarily need to use direct-addressing for this type of integration. For the address syntax in the CFC, have you tried using the format B=[DevInst][ObjectTypeID,ObjectNumber] ? See HERE for a list of Objects and Object Type IDs. In your example, to read Analog Input 0 from device 601110 - the syntax would be B=[601110][0,0]. Another example, to read Analog Input 4, the syntax would be B=[601110][0,4]. Also - for the PXG router, unless you need to use BDT, I would set this to false. It's not always required, but I would also set FDT to True. It's good practice to also define the Max Master number to be equal to the highest MSTP MAC address that you have on the network, i.e. if you have addresses 1 to 20, then set the Max Master to 20. On the PX controller, again not always required, I would set FDT to True. Both the PX and PXG will need to be cleared and re-configured via their Node Setup. Not all devices support transmitting the value on a COV, so you may need to set the polling time of the AI block in the CFC to a value (i.e. 30 seconds) to force the PX to read the value from the MSTP device. Regards, |
5/31/2022 3:11 PM | |
Thanks for the help, I did as you said and now is working. |