7/28/2008 2:30 PM | |
Posts: 8 Rating:
Hello ,everyone! I am a new user, nice to come to here ! our s5 system configuration is as follows: 1. 6es5923-3ua11 2. 6es5928-3ua12 3. 6es5922-3ua11 4. 6av1242-0AB10 5. 6es5525-3ua11 6. some digital and analog modules NowI come into a big problem that both 928A and 922 cpu couldn't enter run state, stop LED on cpu 928 is lit contiuously and stop LED on cpu 922 flash slowly, BASP LED light up after switching on the power supply or Overall Reset and Reset. I don't know where is the fault ,hardware or software or others? pls give some help and suggestion ,thanks! I have also recorded the detailed ISTACK information and corresponding DB1 info in cpu as follows for your reference:
Attachmentistack and DB1 info.zip (543 Downloads) |
7/28/2008 9:07 PM | |
Posts: 2661 Rating:
You should read chapter 6.2 in the following manual: SIMATIC S5-135U/155U System Manual There is a specific sequence for starting a multiprocessor system (described bellow in brief): 1. Jumper settings ok. 2. Coordinator switch on stop. 3. Overall reset both CPU's 4. Load DB1 to both CPU's and start. 5. Start coordinator. You can test each CPU individually after unplugging the coordinator (no power to CC). Regards |
7/31/2008 4:04 PM | |
Posts: 8 Rating:
Hi phantom75 Today I tried to test cpu928 and cpu922 individuly through the coordinator 923 's test function, found that stop LED on cpu 928 flash slowly ,and stop LED on cpu922 flash quickly. the following is the detailed istack info. pls see it . It seems like the I/O modules fault,I didn't power supply the external 24 voltage to the I/O modules , Does itaffect the stop of cpu? THANKS! Attachmentistackinfo.zip (462 Downloads) |
7/31/2008 8:18 PM | |
Posts: 2661 Rating:
Hi seveneleven, Slow flashing means there is a problem and fast flashing means the CPU is demanding an overall reset. In your case the problem is with CPU 928. Do you see other LED's like ADF, QVZ, ZYK? See attachment. Normally this is programmed. That is, you can make the CPU go to stop during address fault. When you were testing,was the EPROM with original program in? Switch on the enable voltage and try. Regards, Phantom75 PS: The main reason for the stop (shown in ISTACK) is missing DB1. That opens up a new line of thought: Program a "test" DB1 (without I/O's), transfer to CPU (after overall reset) and restart. AttachmentPages from pa928ben.pdf (607 Downloads) |