1/15/2022 9:18 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
Hello, You need IM153 module for interfacing. Please refer Operating ET200M as slave on master station CPU315-2DP FAQ for detail information. |
Last edited by: PISCEAN 2010 at: 01/15/2022 11:18:24Corrected IM module number Last edited by: Jen_Moderator at: 01/17/2022 06:02:40Optimized link. |
1/15/2022 4:50 PM | |
Joined: 9/27/2006 Last visit: 9/4/2025 Posts: 12397 Rating:
Hello Arman; Your ET 200M station (IM 153-x slave) is generating an Invalid_Slave_Response diagnostic. See this page from the Felser Profibus Manual on diagnostic telegram bits, check the Profibis diagnostic telegram bit 5 message: https://www.felser.ch/profibus-manual/codierung_der_diagnose.html - Invalid_Slave_Response: Invalid response from slave. This bit is always set to zero by a slave. Here a master notices that a slave gives invalid responses. To understand why thos particular message appears, we need a bit more information on your IM 153-1 or IM 153-2 slave unit (part number, possibly a screenshot of the hardware configuration of the eT 200M station), and it would probably help if you could provide a screenshot of the exact message you are receiving, along with a description of when you receive it. Hope this helps, Daniel Chartier |
This contribution was helpful to
2 thankful Users |
Follow us on