9/22/2014 6:55 AM | |
Joined: 4/19/2008 Last visit: 11/21/2024 Posts: 1525 Rating:
Hello SAMIR, You can Connect 4 RTD to 6ES7-331-7KF02-0AB0 For More Information Look on the Document In Chapter 6.7, You will find the Wiring, it will used 2 Channel for the 1 RTD Connection. |
Ammy |
This contribution was helpful to
1 thankful Users |
9/22/2014 7:04 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
Hello SAMIRKM, No you can't connect 8 RTD only 4 is possible. have a look this thread and read Ayman post Why input card 2 wire and 4 wire do not work |
9/22/2014 8:29 AM | |
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
Hello, The solution was send before did you read it?
Regards, Marcjan |
Problem solved? |
9/22/2014 8:49 AM | |
Joined: 11/7/2011 Last visit: 1/27/2023 Posts: 96 Rating:
DEAR SIR, CONFIGURATION IN SIMATIC MANAGER IS NOT GIVEN. PLEASE HELP. THANKS, SAMIR |
9/22/2014 8:55 AM | |
Hello, It is: page 382 . Regards, Marcjan Attachments7300_module_data_manual_page 382.pdf (457 Downloads) |
Problem solved? |
Follow us on