Hi Guys. can you five me more information/share project/picture about how to run/stop a PLC 1200/1500 from HMI unified please?? Thanks in advance ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 11/04/2024 07:50:47Neue Überschrift nach Splitten |
|
11/7/2024 11:49 AM | |
Joined: 1/21/2013 Last visit: 8/29/2025 Posts: 4087 Rating:
|
Hi, From version 18.0.0.2 it is possible to set the PLC operating state by changing the value of the system tag "@ConnectionName_PLC_OpStateCtrl". To stop the PLC set the value to 4, a value of 8 will put the PLC in RUN mode. Note that you must replace ConnectionName with the name of your connection. Kind regards |