7/11/2018 7:28 AM | |
Joined: 7/9/2015 Last visit: 8/29/2025 Posts: 4443 Rating:
|
Hi, there is a good description for FC105 on Siemens Homepage. Please check this link: How can you standardize and destandardize analog values with STEP 7 V5.5?Towome |
|
|
7/11/2018 9:28 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Is it 2 wire or 4 wire sensor? Have you checked the wiring connections? Have you shortened another AI of the PLC? |
7/11/2018 12:28 PM | |
Joined: 3/9/2017 Last visit: 3/23/2025 Posts: 67 Rating:
|
Mr PISCEAN It is a 2 wire sensor and check the all the connections that are ok.. |
7/12/2018 12:13 AM | |
Joined: 11/12/2008 Last visit: 9/9/2025 Posts: 225 Rating:
|
Hello Dharala, First of all do you calibrated your Load cell indicator for zero scale and span scale, what type of your load cell indicator? do you checked 4 wire or 6 wire of your indicator? - In such as this cases we are usually programming our own Scaling to maintain our analog input that's mean you have to make your scale unloaded ie. on dead load and put down the analog input value and put full scale load and put down the analog input value then make your own scale according to low limit and high limit. - If you need to calculate your process value to get a flow rated for example 8kg per Sec, Min or Hrs. have a look to attached example. Hope that clear. Regards.
AttachmentBelt Scale.zip (495 Downloads) |
Last edited by: H.SAPER at: 7/12/2018 1:29:50 AMLast edited by: H.SAPER at: 7/12/2018 1:48:54 AMHASSAN.S POJAILA |
|