6/18/2016 7:03 AM | |
Posts: 15 Rating:
Indicative of CPU is accordance with Photos. the red LED "SF" is on and i don't know for why? please help me to fix it |
6/18/2016 7:42 AM | |
Posts: 15 Rating:
Performance is correct but this LED is on.!!! |
6/18/2016 7:47 AM | |
Posts: 15 Rating:
who can i do this? |
6/18/2016 9:14 AM | |
Joined: 12/18/2014 Last visit: 9/5/2025 Posts: 35925 Rating:
Look at the Video in attachment. AttachmentDiagnostic.wmv (480 Downloads) |
This contribution was helpful to
1 thankful Users |
6/19/2016 8:13 AM | |
Posts: 15 Rating:
thank you for kindly reply this is diagnostic buffer file. AttachmentDiagnose.txt (470 Downloads) |
6/19/2016 1:44 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
DP I/O station no 5,10,115,116,117 & 118 have failed & as such SF lit RED. Please check those stations. |
6/20/2016 8:45 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
hi, it seams the AI-card has not really a connection to your station. Do you have the right Terminal module? See the manual of the module, which TM´s you can use. SIMATIC ET 200S distributed I/O 4AI I 2WIRE ST analog electronic module (6ES7134-4GD00-0AB0)
hope this helps, regards, |