8/13/2021 11:12 AM | |
Posts: 1 Rating:
|
Dear Expert, I have meet a problem, My Sinamics s120 not detected. I found alarm 400014: Profinet - I/O ramp-up fault type: 1. So I check using software Simatic Step 7 and found that for Profinet module not detected. I think this is broken and i will do a Profinet module CBE20 replacement on Sinamics s120. Other than setting the mac address, are there any more steps that I have to prepare? I hope to get the answer and thank you very much. Best Regards, Febri Irvandro ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/13/2021 13:02:21New subject after splitting |
|
8/14/2021 9:27 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
In Starter you need to complete new configuration of CBE20 (replacement of object is not possible? & in Profinet controller need to modify IP address acordingly. |