1/4/2016 9:16 PM | |
Joined: 9/27/2006 Last visit: 9/6/2025 Posts: 12399 Rating:
Hello torque; Have a look at the attached screenshot, taken from the SITOP UPS 1600 manual: SITOP UPS1600 /
UPS1100 - Siemens Industry Online https://support.industry.siemens.com/cs/ww/en/view/84977415 Basically, the UPS 1600 expects a 24 V DC input to the UPS 1600, with the (one or more) battery modules connected in parallel. This is where your PS 307 should be brought in. The output of the UPS 1600 then feeds the load(s). How long the UPS will feed the loads depends on the current consumption of the equipment downstream of the UPS, and the total Ah rating of the battery module(s) connected to the UPS. A table of backup time vs load current can be found in section 7.3 of the manual. Note the description of the function blocks for TIA Portal and Step 7 v5.5, along with the software SITOP UPS manager, that can be integrated in your program for overview of the UPS functionalities throuhh the user program. You can download all of these from the Automation Technology pages for the UPS 1600: http://w3.siemens.com/mcms/power-supply-sitop/en/dc-ups/battery/pages/default.aspx |
This contribution was helpful to
1 thankful Users |
Follow us on