8/4/2017 2:32 PM | |
Posts: 18 Rating: (0) |
Dear PISCEAN, First I press change soft button to enable the change, (number 1 in the attachement) Then, I write new value and press yellow button (input). Last, I press change button. (number 2 in attachement). However, today I found that all statements gets back to original value when I try to change them. I also entered the password "SUNRISE". May be I do something wrong? AttachmentScreenshots.zip (259 Downloads) |
8/16/2017 1:54 PM | |
Posts: 18 Rating: (0) |
Hello All, It seems I am totally stuck at this stage. I need any guidance. Regards. |
8/22/2017 12:47 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello erenk, Is machine problem solved? If not & if DB31.DBX1.5 value is not getting set =1, please check X axis values in MD 30200, 30210, 30220 & 30230. Please note down & inform here. HTH. |
This contribution was helpful to1 thankful Users |
9/11/2017 10:12 AM | |
Posts: 18 Rating: (0) |
Hello PISCEAN 2010, You can find the MD values in the attached screen shot. Thank you. |
9/25/2017 8:16 AM | |
Posts: 18 Rating: (0) |
Hello All, any advices please? |
10/3/2017 10:59 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello erenk, Please set MD values as below & check. MD 30200 = NUM_ENC = 1 MD 30220 = ENC_MODULE_NR[0] = 1 MD 30230 = ENC_INPUT_NR[0] = 1 MD 30240 = ENC_TYPE[0] = 1 MD 30242 = ENC_IS_INDEPENDENT[0] = 0 After setting these values save the back up & re-power ON system. In PLC area check the DB31.DBX1.5 data bitvalue, it must be 1. If not, you need to go PLC on line & check the logic as why DB31.DBX1.5 bit is not 1. HTH. |
This contribution was helpful to1 thankful Users |
10/12/2017 7:59 AM | |
Posts: 18 Rating: (0) |
Hello PISCEAN 2010, I set the MD values you gave. However, DB31.DBX1.5 value was still 0. I could not find the PLC ladder diagram in the document given by the machine manufacturer. The only information about PLC in that document in attached. (As far as I know, it is an STL diagram) I beg your pardon for lots of questions. But, how can a reach the PLC logic of the machine, do I need an external software? Regards. |
Last edited by: erenk at: 10/12/2017 9:18:00 AM |
|
11/27/2017 1:36 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by pert85 is split to a separate thread with the subject Siemens 840D - 120202 "WAIT CONNECTION WITH CN / PLC". Best regards |