Is it possible to connect 10 IMs to 416F? Each IM has about 4 IO cards. |
5/4/2017 3:24 PM | |
Joined: 9/23/2005 Last visit: 9/15/2025 Posts: 5116 Rating:
|
It says max. 6 IMs supported. |
Regards, |
|
5/4/2017 3:45 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi jacek, where? An IM can also be an DP-slave or IO-device. I don´t think that a 416F can only handle 6 slaves/devices. regards, |
FCK WAR! |
|
This contribution was helpful to
1 thankful Users |
5/4/2017 4:19 PM | |
Joined: 9/27/2006 Last visit: 9/16/2025 Posts: 12409 Rating:
|
Hllo guys; The technical data and installation manuals of the S7-400 may be a bit confusing on this issue of expansion rack IMs, specially for inexperienced users. Yes, you cannot use more than 6 IM460-0/1 for example with a S7-400 central rack. However, the total number of IMs shown in the ocumentation in a system is 21. The attached screenshot from the S7-400 module data will explain why: The IM 460-1 (SEND IM) in the central rack can attach to up to 6 IM 460-0; one IM 460-3 in the central rack can connect to up to 6 IM 461-3 in their expansion racks. So the total combination of Expansion racks available is 21 in a S7-400,; the maximum nuer of the different IMs to connect to these expansion racks is more limited. Look at the Technical Data for the CPU 461F-2 as an example, go down to the Hardware Configuration /Interface modules section. https://support.industry.siemens.com/cs/pd/693839?pdti=td&lc=en-FR These expansion racks and interface modules allow you to use S7-400 I/O modules and CPs in deported racks outside the CPU central rack. If you do nor mind using S7-300 modules for example you could also use Profibus remote racks, as ET 200M systems with IM 153-2, or Et 200S/ET 200MP deported I/O systems. There you could have as many as 124 seperate I/O racks, using Profibus-DP standards. Hope this helps, |
This contribution was helpful to
1 thankful Users |
Follow us on