11/12/2022 12:41 PM | |
Joined: 9/4/2021 Last visit: 11/18/2022 Posts: 3 Rating:
|
Hi to all. I have a LOGO! 6ED1052-1FB00-0BA8 with firmware V81.02. Can it support Modbus? [snip] ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/14/2022 10:21:33New subject after splitting. Division of questions into separate topics. |
|
11/14/2022 11:58 AM | |
Joined: 12/18/2014 Last visit: 9/16/2025 Posts: 35965 Rating:
|
The LOGO! with the order number 6ED1052-1FB00-0BA8 isn't a SIPLUS LOGO!. The SIPLUS version has the order number 6AG1052-1FB08-7BA0. See here: 6AG1052-1FB08-7BA0 This both LOGO!s supports Ethernent TCP/IP with the S7 protocol and also Modbus TCP/IP. Not supported are Modbus RTU or Modbus ASCII. |
This contribution was helpful to
1 thankful Users |
11/15/2022 9:26 AM | |
Joined: 9/19/2018 Last visit: 12/6/2024 Posts: 399 Rating:
|
The combination of order number and firmware version you named doesn’t exist. For Modbus TCP you need at least *08-0ba0. This has then a firmware version V1.81.01 or higher. It’s not possible to update firmware of a LOGO! 8.0 (*08-0ba0) at all. |
Last edited by: LOGO! Support at: 11/15/2022 10:10:35 |
|
11/15/2022 9:50 AM | |
Joined: 12/18/2014 Last visit: 9/16/2025 Posts: 35965 Rating:
|
Sorry, that's not correct. LOGO!s with the order number 6ED1052-XXXXX-0BA8 and a firmware version V1.81.01 or higher supported Modbus TCP. The LOGO!s of the 1. generation (0BA8.Standard or LOGO! 8.0) and LOGO!s of the 2. generation (LOGO!8.FS4 or LOGO! 8.1) had the same order number, which led to a great deal of confusion at the time. They differ in the FS status and the firmware version. AttachmentVersions of 0BA8.txt (1111 Downloads) |
This contribution was helpful to
1 thankful Users |
11/16/2022 10:01 PM | |
Joined: 9/4/2021 Last visit: 11/18/2022 Posts: 3 Rating:
|
Thanks a lot for your responses! I made the Modbus communication via Virtuino IoT app. |
Follow us on