1/9/2014 7:51 AM | |
Joined: 10/7/2005 Last visit: 9/14/2025 Posts: 3049 Rating:
|
Hello Vibha getting the manual for your S5 110A is no problem and available for downloading at Programmable Controller S5-110A Programming Instructions. So much for the good news and here comes the bad: - Unless your CPU has an EPROM in it it that you can read out, you needto add the 500 programmer interface module to your system togo online(see page 9 of the above manual) - You need an old PG with an old Step 5 versionto read at and look at theprogram, seeHERE and HERE for more. Let's say you overcome all the above hurdles, the last task is to manually program the new S7 as per original S5 logic (110A S5 programs are all contained in one long linear block and can not be converted with the S5 to S7 converter). I hope this helps |
Cheers |
|
1/10/2014 5:59 AM | |
Posts: 12 Rating:
|
Thank you fritz. |
Follow us on