7/16/2014 9:37 PM | |
Joined: 12/1/2009 Last visit: 7/14/2025 Posts: 672 Rating:
|
Hi Navnag, active bus modules are required when you want to remove/plug IM/IO modules in RUN. If you can afford to switch your system into STOP mode in these cases they are not required. We always use active bus modules in our H-Systems whileacomplete systemshutdowncosts the client a fortune. On the other hand - if they pay for it ? Best Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to
1 thankful Users |
7/17/2014 7:24 AM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello TIBI68 Well we do not have a choice when using tradational ET200M with Profibus Redundant communication with S7-400H as it will not work without active bus modules regardless of whether we need Module Change during runtime or not . I understand this is because bus has to be switched between one of the two IMs. I understand from your post that I can use ET200M with Profinet ( S7-400H - PN network ) without Active bus modules ( If I do not need need Module replacement in Run facility ). In any case there is only one IM and no Bus switching is needed. Thanks indeed Cheers Navnag |