10/30/2015 8:44 AM | |
Joined: 1/27/2015 Last visit: 7/22/2024 Posts: 53 Rating: (9) |
Hi Alfredo@as99 did I get you right? You already registered your Modbus product and received a REG-Key from the license team? Your matter sounds a little strange. Because if the license for modbus is missing the SF-LED will blink and not be steady on. You wrote the license bit is 'true" but the Reg-Key is empty? That also can not be. Maybe their is an other fault in your program (like a calculation error) which will call the OB121, and so if its missing the CPU stops and turns on the SF-LED. Did you try to comment out the modbus function for test? Just to see if the CPU stop comes really from the modbus function block.
Greetings Bachgeist |
10/30/2015 1:19 PM | |
Joined: 12/7/2011 Last visit: 11/10/2024 Posts: 384 Rating: (9) |
Hi Bachgeist, thanks for your reply, yes i did it, i've already registered my licence. I'm pretty sure that the problem is the licence because if i sart the cpu without the OB121, doesn't start and in the buffer i see the cause of the stop from the first call of the modbus. I don't know if could be the reason of the problem, but in my project i've two comunication in modbus tcp for two different devices. Do you think could be that? i've attached my db's Regards. AttachmentModbus licence.pdf (326 Downloads) |
11/2/2015 9:08 AM | |
Joined: 1/27/2015 Last visit: 7/22/2024 Posts: 53 Rating: (9) |
Hi Alfredo@as99, as I can see the license key is valid, so this is not the problem. Did you uncommend the modbus function for test, what else the problem could might be?
Regards bachgeist |
Follow us on