11/1/2017 6:25 AM | |
Joined: 12/18/2014 Last visit: 10/5/2024 Posts: 33880 Rating: (4214)
|
The correct syntax by using the datatype BYTE is: The correct syntax by using the datatype BIT is: But the datatype can you only use with the right Firmware of the CMR. Is the Version of your CMR not V2.0, then you must update the firmware. Follow the link: Firmware update V2.0 for LOGO! CMR2020 (6GK7142-7BX00-0AX0) and LOGO! CMR2040 (6GK7142-7EX00-0AX0) And also you must have the right LOGO! with the right firmwareversion by using datatype BIT: LOGO! FS04 or higher (firmware Version FW V1.81.01 or higher) |
This contribution was helpful to1 thankful Users |
11/1/2017 2:36 PM | |
Posts: 5 Rating: (0) |
Hi, Thanks for quick response. I have to update fw versions. Please see CMR and LOGO! current firmware version in attached file. |
11/1/2017 2:57 PM | |
Joined: 12/18/2014 Last visit: 10/5/2024 Posts: 33880 Rating: (4214)
|
The firmware of the LOGO! is FS05 (V1.81.02). That's ok, but there is a update for FS06 available: Product information on the firmware update for LOGO! 8 FS:04 and FS:05 |
11/2/2017 3:18 PM | |
Posts: 5 Rating: (0) |
Now it's working. |
This contribution was helpful to1 thankful Users |
Follow us on