7/28/2010 2:10 PM | |
Posts: 13 Rating:
|
Yes it is CP341 , but I want to know any other Commn cards are to be installed at DCS |
7/29/2010 7:30 AM | |
Posts: 130 Rating:
|
Hey prks, There is no need to install any other cards on the DCS side...... Yokogawa has a built in modbus interface (Communication Gateway Unit)in its DCS system......All you gotto do is interface with that card through our CP341. Else, the best way to go is through OPC. regards, |
7/29/2010 9:05 AM | |
Posts: 130 Rating:
|
Hey prks, I have understood that, Yokogawa has to supply the following card in the DCS for easy integration of SIEMENS system into their DCS. Model LFS9055 Siemens Communication Package (for ACM11, ACM12) AttachmentDoc2.pdf (238 Downloads) |
7/29/2010 12:47 PM | |
Posts: 13 Rating:
|
Thanks Ammy & Pratap. |
7/29/2010 12:48 PM | |
Posts: 13 Rating:
|
Thanks Ammy for your info |
7/29/2010 2:27 PM | |
Posts: 3093 Rating:
|
Hello Prks, when you want to use the protocol ModbusTCP you need a CP343-1 or PN-CPU and the ModbusTCP library: http://www.industrysolutions.siemens.com/industrial-services/it/en/PRODUCTS/SIMATIC_ADD_ONS/S7_OPEN_MODBUS_TCP.HTM Regards, Kaulquappe |