Isn't there anyone to help me out ? |
3/28/2023 1:59 PM | |
Joined: 5/17/2016 Last visit: 7/2/2025 Posts: 1 Rating:
|
Use I-Device. On Profinet RT you can get those two S7-1200 exchange data with up to 1ms update time. You can find more info here: Tip: I-Device IO-Controller communication - 188282 - Industry Support Siemens You simply configure one of the S7-1200 as an I-Device (maybe the one with the encoder), other S7-1200 is and IO-Controller. Thanks, Mirek |