Hi to all, I have a problem withComunication between WinCC 7.2 and S7-1500 cpu. In WinCC project i have configured the "SIMATIC S7-1200 S7-1500 Channel" as in the attached file. CPU side, i have only configured the IP addres, set the "full access (no protection)" in the cpu property, and unset the "Optimized block access" in the DB property that i want to read. When i start the runtime, the comunication stay disconnected and i dont knows why. The strange thing is: In the comunication manual, i read:"Select in the context menu of the channel unit "TCP / IP" the Newconnection. "This will open the dialogConnection Properties ". But, as you can see in the attached file, there is no one"TCP / IP" channel but only "OMS+" Could anyone help me. Thanks Alfredo. AttachmentBinder1.pdf (1696 Downloads) |
Last edited by: Alfredo@as99 at: 9/11/2013 5:08 PM |
|
9/13/2013 2:42 PM | |
Joined: 12/7/2011 Last visit: 8/16/2024 Posts: 384 Rating: (9) |
I billwest, As you can see in the attached file, i have checked the acces point in the PG-PC interface, but the problem still present. I dont know what i wrong, but in can not fix the problem. One question: I have to also install the SIMATIC NET for a right functionality? Thanks Alfredo
AttachmentAcces point.pdf (1631 Downloads) |
Last edited by: Alfredo@as99 at: 9/13/2013 2:43 PM |
|
9/13/2013 3:10 PM | |
Posts: 510 Rating: (117) |
Yes! you must install SIMATIC Net. billwest |
9/13/2013 5:36 PM | |
Posts: 510 Rating: (117) |
Here is a link for SIMATIC Net Compatibility: http://support.automation.siemens.com/WW/view/en/9859007 SIMATIC Net V7.1 is compatible with WinCC V7.2 and Windows XP SP3 SIMATIC Net V8.2 SP1 is compatible with WinCC V7.2 and Windows 7 64 bit with or without SP1, Windows 7 32 bit with or without SP1, Windows Server 2008 R2 SP1Standard or Enterprise 64 bit These are the choices avaialble to you. billwest |
This contribution was helpful to2 thankful Users |