Hello black_star, you can use the PN interface of IM151-8. A license of 2XV9 450-1MB02 is required. All necessary information can be found on www.siemens.com/s7modbus. There you will also find a download application for a demo version of the library. Regards, Kaulquappe |
This contribution was helpful to2 thankful Users |
5/13/2014 8:21 PM | |
Posts: 9 Rating: (0) |
this was so helpful , thank you very much Kaulquappe .& SolutionFinder . |
Last edited by: black_star at: 5/13/2014 8:22 PMLast edited by: black_star at: 5/13/2014 8:22 PM |
|
5/15/2014 9:49 AM | |
Posts: 9 Rating: (0) |
hi guys.. is there any limitation for the distance between the ET200S station and the third party system ? it will communicate up to how long ?? |
5/15/2014 10:13 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Hello black_star For Modbus TCP/IP - The distance limitations imposed by Ethernet Hardware apply. Maximum Recommended distance between two Etnernet switches is 100m ( with Electrical network. ) Can be increased by going in in between switches orby using a F.O. network with F.O. switches. ( May be upto 4km with Multimode Fiber ) and much more with Monomode FIber network. For ModbusRTU - The distance limitations imposed byRS485 Hardware apply. For a typical baud rate of 9.6kbps the distance can be upto 1200 meters ( With good quality screened cable ) Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
7/30/2014 3:26 PM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating: (135) |
New question was split to Communicate IM151-8 PN/DP Cpu with Third party drives over modbus RS485 Protocol. Best regards O_Moderator |
9/9/2014 3:50 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by Arunrajeis split to a separate thread with the subject one port for PC (SCADA), can I use other port for Modbus TCP/I?. Best Regards Min_Moderator |