8/3/2023 2:43 PM | |
Joined: 6/11/2019 Last visit: 9/15/2025 Posts: 2630 Rating:
|
Hello Andrus_Saar, exactly this topic was discussed recently in the German part of the forum (see here). Greeting Ella_68 (translated with Google) |
8/3/2023 3:15 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35964 Rating:
|
But this solution in the german speaking part of the forum works only when the minimum value of the limiting is 0. |
8/3/2023 5:55 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35964 Rating:
|
For the web server I found a solution. See attached screen video. If a value outside the allowed range is entered, it will not be accepted and the last valid value will be written back into the input field. AttachmentOnline test.zip (511 Downloads) |
8/3/2023 5:58 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35964 Rating:
|
Here the LOGO! program and the LWE project.
AttachmentSetpoint limiting.zip (677 Downloads) |
8/6/2023 2:45 PM | |
Joined: 10/15/2022 Last visit: 9/11/2025 Posts: 68 Rating:
|
Hi, Ella_68 , Ixo65 and others!
After several hours (and days) of playing, I got the aforementioned program to work as it should by slightly modifying it. After programming, start value is 15, limits are 10 and 20. The counter value can be changed with the keys ESC+< and ESC+> or by entering the value. Program tested on LOGO!8 6ED1052-1MD08-0BA1 (firmware 1.83.02). Andrus ---------- 06.08.2023 Added some additional VMs late at night. AttachmentCounter limit test 2.zip (518 Downloads) |
Last edited by: Andrus_Saar at: 08/06/2023 14:55:49Last edited by: Andrus_Saar at: 08/06/2023 15:33:05Last edited by: Andrus_Saar at: 08/06/2023 19:24:02 |
|