2/7/2023 11:23 AM | |
Joined: 2/17/2020 Last visit: 9/11/2025 Posts: 1251 Rating:
|
Hi, Please see: |
A rating will be well appreciated. |
|
This contribution was helpful to
1 thankful Users |
2/7/2023 11:25 AM | |
Joined: 1/21/2013 Last visit: 9/11/2025 Posts: 4102 Rating:
|
Hi pattanaik_BBSR, you can use the S7 communication or you can use the Open User Communication (OUC). The S7 communication is the easier way, but due to the reduced feature set of the CP 343-1 Lean you would only be possible to program the communication on S7-1500 side using PUT/GET commands. For OUC you have to use AG_SEND/AG_RECV for the S7-300 and the T-functions for the S7-1500. Kind regards |
This contribution was helpful to
1 thankful Users |
2/10/2023 12:46 PM | |
Joined: 8/3/2009 Last visit: 9/11/2025 Posts: 16400 Rating:
|
Hello pattanaik_BBSR Here you can see in Chapter 21.4.5 what is possible: https://support.industry.siemens.com/cs/ww/en/view/78028908 Bye Murof |