2/2/2016 9:33 AM | |
Posts: 10 Rating:
|
Hello guys, did someone find something? I have a similar problem. I have a CPU1214C connected with an IPC277E with WinCC RT Adv. (v13 Sp1 Up 6) At this step everything is fine but then when I add my OPC Server, it switch my HMI connection into Softbus. After that my IPC and my PLC aren't working together. ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 2/2/2016 12:16:39 PMNew subject after splitting |
|
2/2/2016 2:02 PM | |
Posts: 10 Rating:
|
Problem solved |
This contribution was helpful to
2 thankful Users |
2/3/2016 10:13 AM | |
Posts: 10 Rating:
|
Hi! I worked on this to find out a better solution and I want to share it. I put the S7 connexion and the HMI connexion on the same port, and this time it works well with the Softbus connexion. In the IPC properties I forgott to select the Station PC. Take care that on the IPC the Station Configuration Editor has the same name as in the project and that the Index is corresponding to the HW-Config. AttachmentIPC with OPC and WINCC RT on TIA PORTAL.pdf (370 Downloads) |
This contribution was helpful to
1 thankful Users |