Hi , I recently had the same problem as AutoGen_3679175 in a PXC100.E-D, however, in my case I'm doing the download thought a BBMD Device. So my network cards are in different networks with a different subnets. With the same configuration, I did partial and full download to PXC7.E400M with no errors. Any ideas what could be in my case? Thank you PXC100.E-D - FW=6.30.018 PXC7.E400M - FW=V02.20.172.37-19679 ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/05/2024 06:50:57New subject after splitting |
|
2/2/2024 12:25 PM | |
Joined: 3/1/2018 Last visit: 11/14/2024 Posts: 58 Rating: (24) |
Hello, If XWP is in different IP segment to the automation station FDT on AS should be enabled. Regarding the subnets, when PC is in wider range of network addresses than the AS communication is possible, but sending files such as config files causes errors (I don't know why). Please check materials in attachment regarding FDT & BBMD Best regards. Attachment20_BBMD & FDT.ppt (477 Downloads) |