3/12/2014 3:27 PM | |
Posts: 220 Rating:
|
Hi john, for PCS 7 it's adviced to use just hardware which is testet for PCS 7. This can you find when you change the Profile in the HW-Config to your PCS 7 Version. Don't use the Standard-Profile. HereYou can find the Manual with the released Modules for PCS 7 V7.1 xxx. |
3/12/2014 3:39 PM | |
Joined: 9/27/2006 Last visit: 9/2/2025 Posts: 12397 Rating:
|
Hello brothersjohn; I have not worked with the Dräger gas detection system, but I have a few thoughts that might help, with any luck, First point: you error message seems related to the version of the Regards Profibus interface, it states that it is expecting a Version 20.79, and you have selectd a version 21 from you Profibus catalog. Try replacing the module with Vers. 20 and see if the error message changes. Second point: the Regard system is a non-redundant Profibus-DP slave, so it cannot be connected to bith masters in a redundnt configuration, as seen in your HWConfig picture. If you want toconnect the Profibus information from your gas detection systm redundantly, you should use what is known as a Y Link, which ius designed for such connections. Here is some information on the Y Link for your examination: SIMATIC Bus links DP/PA coupler, active field distributors, DP/PA Link and Y Link In case others are interested in theDräger Profibus interface, here is some documentation I located on the web: Dräger REGARD PROFIBUS-DP Gateway http://www.search-document.com/pdf/1/3/drager-regardcontrol-system-operators-manual.html Hope this helps, Daniel Chartier |
Follow us on