(0)| 12/16/2022 6:48 AM | |
|
Joined: 3/2/2021 Last visit: 9/28/2023 Posts: 14 Rating:
|
Hi Duris_I and everyone. I found the reason why this error happend. The firmware of my new PLC is 1.22 that not support Mode 12 of HSC0. You can see clearly in the attached files that if I select the firmware of PLC in the project is 1.22, the Mode 12 of HSC0 disappear. But if I select the firmware of PLC in project is 2.00, Mode 12 of HSC0 appears. This's *** error. Thanks Duris_I for spent your time with me. Regards., Lodolfo AttachmentResult.zip (990 Downloads) |
Last edited by: Jen_Moderator at: 12/16/2022 09:01:56Inappropriate word removed. |
|