1/11/2006 8:49 AM | |
Posts: 3 Rating: (0) |
Thank You McMurphy, I'm still searching information about this. |
1/21/2006 11:25 PM | |
Posts: 54 Rating: (5) |
It is not possible to make a direct connection via ethernet from an S7 CP 343-1 to an AB L32E. The problem is that S7 speaks S7 protocol and the AB speaks CIP protocol. They cannot understand each other even if they are both on ethernet. Your options are: - Use a PC with OPC Server and OPC Client software as a go-between. But a PC is obviously not as reliable as PLCs are. - Use Profibus in stead of Ethernet.Hilscher has Profibus modules for the AB Compactlogix range. |
Last edited by: JesperMP at: 1/21/2006 11:27 PM |
|
1/30/2006 9:19 AM | |
Posts: 3 Rating: (0) |
Thanks Jesper, I look for the Profibus solution now and hope it will be the good. Bye |
Last edited by: siemall at: 1/30/2006 9:19 AM |
|
2/3/2006 12:07 PM | |
Posts: 54 Rating: (5) |
The CompactLogix does not support "raw" UDP communication. The only protocol supported is CIP on Ethernet/IP. |