Hi all, I've found some thread in forum about this topic, but it's discussion about using T blocks. Not all S7-300 CPU and CPs support T blocks and open TCP communication. I've tried to use open ethernet example and saw that I get error and diagnostic says that SFC131,SFC133,SFC134 is not loaded. So I can't use open ethernet on S7-300 side. So is it any possibilty to pragram connection between S7-314C-2DP with 343-1 LEAN CP and S7-1200 ? |
Best regards, |
|
12/4/2009 2:33 PM | |
Posts: 5822 Rating: (412)
|
Dear Darius, I am not sure... but the T-Communication and especially its SFCs are only implemented to the PLCs carrying a PN interface. Therefore the use of T-Functions with S7-CPUs without PN interface will certainly not work. |
12/4/2009 3:33 PM | |
Posts: 5822 Rating: (412)
|
I like short and simple answers.... YES. J_Bell |
This contribution was helpful to1 thankful Users |
12/5/2009 2:57 PM | |
Joined: 9/28/2005 Last visit: 11/5/2024 Posts: 2957 Rating: (242) |
Sometimes one word means very much..... Thanks. |
Best regards, |
|
1/6/2010 11:33 PM | |
Posts: 32 Rating: (0) |
Hi, Can you helpme with an example project about this topic. If can you send the S7-300 and S7-1200 project, I'll grettings so much. |
1/21/2010 4:23 PM | |
Posts: 5822 Rating: (412)
|
Hello Darius, thank you very much for telling your latest status, may you let us know what the solution for the problem was? Thank you in advance. J_Bell |
1/22/2010 7:09 AM | |
Joined: 9/28/2005 Last visit: 11/5/2024 Posts: 2957 Rating: (242) |
Hello, The problem was that S7-300 side AG_SEND function was sending continuously (ACT = TRUE), so sometimes connection was hung. Especially right after restart of PLC or after you break connection and restore again. So it was solved by changing program that AG_SEND sends on time pulses or what is even better taking in account DONE signal. Then you send as soon as previous job is finished. Solution about connecting S7-300 with S7-1200 via ethernet is provided here http://support.automation.siemens.com/WW/view/en/40556214 |
Best regards, |
|
This contribution was helpful to2 thankful Users |