5/21/2008 1:00 PM | |
Posts: 124 Rating: (17) |
I'm not sure if I understand correctly you problem so I'l talk based on my understanding. Here are some sugestions:
|
5/22/2008 6:06 AM | |
Posts: 83 Rating: (1) |
Thanks dchartier. Have a nice day! hgq |
5/23/2008 10:25 AM | |
Posts: 83 Rating: (1) |
Hi Sevab, Thanks forinfomation. If I understand correctly, the safety integrity level does not depand on the numbers of contact being checked for each signal. Please find attachment (abstracted from sheet 82 of 198, Siemens manual S300f_e.pdf), in which only single contact is usedhoweverthissetupcould achieve SIL3. Regards, hgq AttachmentF-DI Setup.pdf (418 Downloads) |
5/23/2008 11:03 AM | |
Posts: 83 Rating: (1) |
Hello, May i change my question for this issue. Firstly please open the attachment, in which there is two typical setups. Setup 1. Single contact connected to oppsing channels; Setup 2. Dual contact respectively connected to oppsing channels. In setup 1, the discrepancy time between both channels merely depens on the response time difference between left channel and right channel. According to hardware manual, the response time is maximum 3 ms, either from "0" to "1" or from "1" to "0". Therefore the maximum discrepancy time is 3 ms. It should be reasonable to assume that the discrepancy time is nearly zero since the left channel and right channel are in the same module and both are electronic. In setup 2, the discrepancy time depends on the mechanical reation of both contacts, which may be significant comparing to setup 1. My arguement is In setup 1, 10ms for discrepancy timeremaining as default is sufficient. In setup 2, the setting for discrepancy time can be bigger depanding on the mechanical reaction of both contact and the application requirement. Is thisanalyzingcorrect? Regards, hgq Attachment1 contact & 2 contacts.pdf (447 Downloads) |
5/27/2008 5:40 AM | |
Posts: 83 Rating: (1) |
Hello, I would appreciate more comments from safety experts. Thanks hgq |
Follow us on