Joined: 7/7/2023 Last visit: 4/25/2024 Posts: 30 Rating: (0) |
TIA PORTAL V17 s7-1500 R/H-Station -> CPU 1515R-2 PN -> V2.9 Thanks, Sergio |
7/7/2023 9:20 AM | |
Joined: 1/21/2013 Last visit: 5/2/2024 Posts: 2735 Rating: (443)
|
Hi Sergio, PUT and GET are two of the instructions not supported by S7-1500R/H redundant system. Kind regards |
This contribution was helpful to1 thankful Users |
7/7/2023 9:22 AM | |
Joined: 7/7/2023 Last visit: 4/25/2024 Posts: 30 Rating: (0) |
And from a PLC1200 that does not have redundancy, could I read data through a GET? or not?. Thanks
|