2/14/2023 6:05 AM | |
Joined: 1/21/2013 Last visit: 9/12/2025 Posts: 4108 Rating:
|
Hi kaviPLC, would you please provide more information? The CPU 1517F-3 PN/DP, V2.9 (6ES7517-3FP00-0AB0) allows 288 connections via integrated interfaces where 10 are reserved for ES/HMI/web. So from that point of view, there should not be any problem. Kind regards |
2/15/2023 5:58 AM | |||
Joined: 3/11/2019 Last visit: 9/1/2025 Posts: 1653 Rating:
|
Hi kaviPLC, CPU 1517 allows up to 288 connections via integrated RJ45 interfaces, as already mentioned by Stefan. From these 288 connections, are 10 reserved for HMI, bu you can use many more. But what CPU with which firmware are you using really? Because as seen in your screenshot, only 4 are "reserved". Nevertheless, in your screenshot you can also see, that you have 278 connections "dynamic", these can all be used. CPU 1517F-3 PN/DP, 3MB Prog., 8MB Data
How can you optimize an HMI connection and what has to be considered regarding the connection resources? (HMI operator panels with S7-1200 or S7-1500 controllers)regards sancruz |
||
Feedback appreciated, please rate |
|||
This contribution was helpful to
2 thankful Users |