1/19/2021 8:56 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Please check the part number you mentioned. Best way is attached snap of drive/part number. |
1/19/2021 5:48 PM | |
Joined: 3/27/2008 Last visit: 9/14/2025 Posts: 1216 Rating:
|
SIEMENS MICRO MASTER6SE3113-6BA70-4AAO Input1 ph 230v 6.5A 47-63Hz Output3 ph 3.4A 0-650Hz Motor750W Serial No. XAG025MM195F Issue F Reply: From the serial number this is the date and place of manufacture.. Congleton, Cheshire, 1996, 2nd May. MM75* 1 AC 230 V 750 W 6SE3113–6BA40 The above is the close to the number you have supplied? The part number appears to be a bit adrift, but I have attached a manual which I believe applies. The display is flashing, indicates a warning, for a fault the display shows F---- codes see manual. Does the display flash with the motor disconnected? You should be able to disconnect the motor and give it a run command, and the display should show a value for frequency as it ramps to speed. Whilst this inverter is producing 230 Volts 3 phase, connected this is a single phase motor with a capacitor for the phase shift, the second phase, can you replace the capacitor? The PWM output from the inverter will stress the capacitor, so worth having a look at this, after 24 years? See how this goes, come back if I can help further, it has been some time since I have had a go with one of these Micromasters, designed developed and manufactured in the UK. Tractor AttachmentG85139_E1720_U325_B_En.pdf (675 Downloads) |
Last edited by: Tractor at: 01/19/2021 18:12:50Last edited by: Tractor at: 01/19/2021 18:17:22Tractor |
|
This contribution was helpful to
1 thankful Users |
Follow us on