7/15/2009 7:06 AM | |
Joined: 9/27/2006 Last visit: 9/16/2025 Posts: 12409 Rating:
|
Hello Kadhar; Fisrt thoughts: How did you connect your channel, and what type of sensor have you connected? You could have 2-wire (powered from the Analog module) or 4-wire transducer (powered from its own power supply). If you connected a 4-wire as a 2-wire unit, you will expect to have an overflow (double the input current...). Also, make sure all you M- pins are shorted anmd connected to earth, this limits measuring errors due to cross-channel interference See the attached dioagram, extracted from the S7-300 Module data manual; It shows typicalwiring diagrams for 2- and 4-wire transducers on your analogmodule. http://support.automation.siemens.com/WW/view/en/8859629 Hope this helps, Daniel Chartier |
This contribution was helpful to
1 thankful Users |
7/18/2009 3:03 PM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
Dear Daniel Chartier, Dear Ayman Elotaify, Giving you all respect and expertise but I couldn't figure out how double current would flow in the circuit. I hope you can illustrate it little bit more. I don't know howconnecting 4-wire transducers as 2 wire transducers according to wiring diagram of 1KF01 module will double the current. I'll assume that measured physical valueshouldgive8 mA, and the 4-wire transmitter will try to force that 8mA in a certain direction then how would that 8 mA be doubled to 16 mA? Pleasecomment onthe attached file. Then, It seems to me that Mr. Ayman has mixed up between the case we have (1KF01) and other active modules (7KF02 for example).
Actually the channel/moduleshouldn't act as a current source even if it is an active channel (with potential across its terminals). It just applies potential across the terminals but the current is varied by transmitterand is totally depending onmeasured physical value. One more important thing is thatthe 1KF01 will always act as a passive module. Back to the main problem, Sometimes, transducers/transmitters are configured to give 21mA when they have internal error or extreme overload. So, at PLC side, when it receives this 21mA, it will mean something is wrongwith transmitter. Best regards. H-H Attachment4 wire VS 2 wire.pdf (616 Downloads) |
Last edited by: H-H at: 7/19/2009 12:04 PMEdit : I deleted some words and put them again. Sorry for inconvenience Last edited by: H-H at: 7/19/2009 11:43 AM |
|