6/16/2011 1:20 PM | |
Posts: 21 Rating: (0) |
It is siemens 840d with PCU 50. i have tryed to clear S3 and S4 but still this alarm is comming |
6/16/2011 2:43 PM | |
Posts: 21 Rating: (0) |
on NCU 1st row green LED is glowing 2nd row two RED LED are glowing and setting is displaying"6" . I have checkd the NCU battery and replaced the same already. |
6/16/2011 3:09 PM | |
Posts: 2964 Rating: (482)
|
Look's like clearing is not done proper..... Check this link: /tf/WW/en/Posts/59362 Regards, Ekalavya |
Last edited by: EKALAVYA at: 6/16/2011 3:19 PMlink added |
|
6/17/2011 12:21 PM | |
Posts: 2964 Rating: (482)
|
Hello, Fine your getting the same alarm.... Alarm 300300 :Axis boot error Error occurred while starting up the displayed drive. (Example: Drive signals timeout). Meaning of the error code: - 0..5: Timeout while waiting for the acknowledgement from the drive in the displayed state Could you check this following things.... >Disconnect the all the cables on the NCU card just connected I/R module and the NCU with MPI cable connected. No encoder and power cable to connected. Clear your NC PLC. > When your clearing your NC-PLC are you find 6 indicated in your seven segment display and 2 green leds are getting displayed if this indaictes then your clearing is proper or error led is there...does red led shows in NC or PLC leds are flashing.... > After clearing NC PLC are you directly loading your backup...looks like your loading.... > Can you load your PLC first and check whether its healthy conditionyou need to connect the cable i.e on x121 cable should be plugged. > After thiisconnect one by one drive i.e Encoder and power Commission your NC parameterconfigure thedata manually.(General MD-Channel MD-Drive Configuration -Axis MD-FDD/MSD) >Whileconfiguring one by one drive if you are find a error then you need to physically correct this may be there Hardware problem(611D and LT Module) > Configuration happens smoothly fine...butstill your facing same problem means then there is problem in the NCU card. If you have any spare NCU card of same type replace and check it.... Attaching the PDF document for configure Drives in 840D. Regards, Ekalavya AttachmentProcedure to configure Drives in 840D final 1.pdf (753 Downloads) |
This contribution was helpful to1 thankful Users |
5/27/2016 3:14 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by kothari_1 is split to a separate thread with the subject 840d, all light flashing and alarm message. Best regards |
5/31/2016 11:32 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by Shameej is split to a separate thread with the subject error code 2001. Best regards |
Follow us on