6/27/2013 4:16 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating:
|
Hello You do not need any GSD File for 6ES7 972-0AA02-0XA0 and I don't think any GSD file is available. GSD file is only required for diagnostic repeater . The RS485 bus repeater can be used for MPI / Profibus networks and can be installed as per guidelines given in its manual : http://support.automation.siemens.com/WW/view/en/48556312 It does not have to be shown in the hardware configuration of PLC. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to
1 thankful Users |
6/27/2013 7:00 PM | |
Joined: 4/17/2012 Last visit: 8/14/2024 Posts: 474 Rating:
|
|
Last edited by: DS SURESH KUMAR at: 6/28/2013 7:47 AM |
|
6/29/2013 8:58 AM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating:
|
Hi dhinagaran.v, Give us your hardware configuration, so we can see how it is made and tell us what you want to do. |
6/29/2013 1:49 PM | |
Joined: 10/7/2005 Last visit: 8/9/2024 Posts: 3016 Rating:
|
Hello dhinagaran.v pleasecheck if you ticked "Test, commissioning,routing" in the DP interface properties of your DP Slave CPU. Attached is a pic that shows you were to find it and you'll find that ticking this box will considerably speed up online programming access to the DP Slave CPU. |
Cheers |
|
This contribution was helpful to
2 thankful Users |