6/30/2009 7:45 AM | |
Joined: 3/21/2006 Last visit: 3/30/2025 Posts: 10239 Rating:
|
Hello, Follow explanations (example) from manual - DP/DP Coupler Regards Hristo MIhalev |
6/30/2009 8:15 AM | |
Posts: 49 Rating:
|
Helllo BOSS Please find application example for the DP/DP Coupler configuration. Direct Data Exchange between separate PROFIBUS DP Systems via DP Communication Regards, Enigma |
6/30/2009 9:41 AM | |
Joined: 4/24/2006 Last visit: 9/15/2025 Posts: 9027 Rating:
|
Dear THE BOSS, Have you seen this link: Whatshould you watch out for when configuring a CP342-5 as DP master? Best regards, Wizard |
7/1/2009 6:08 AM | |
Posts: 15 Rating:
|
Hello UMENCHO, Here i am sending u the hardware configuration of two plcs and dignostics of CP-342-5. Thank u. AttachmentFOR SIEMENS.zip (861 Downloads) |
7/1/2009 7:35 AM | |
Joined: 10/7/2005 Last visit: 9/14/2025 Posts: 3049 Rating:
|
Hell the Boss you HWconfig looks ok, but the attached example does NOT have the S7 program in it. My guess is the problem lies with your handling of the DP_SEND and DP_RECV calls. Have another look at the link that Wizard mentioned and bear in mind especially the followingconcerning your setup: You highest Output address for the DP/DP coupler (on the CP342-5 side) is 691. This meansyour DP_SEND DB must be 692 bytes long. Similarily, your DP_RECV DB must be 596 bytes long (highest Input address is 595, you always start with I/Oaddress ZERO if you use a CP342-5 and this is commonly misunderstood). I hope this helps |
Cheers |
|
Follow us on