Hi crkz94, ethernet only describes the physical layer and the data link layer. It can only be a part of a communication protocol. What we are interested in is, do you use S7 protocol, OPC UA or something different? What SCADA system do you use? Kind regards |
9/30/2022 9:04 AM | |
Joined: 10/11/2021 Last visit: 4/10/2024 Posts: 15 Rating: (0) |
Hi Stefan, We are using S7 protocol and it is word about IGNITION SCADA. |
9/30/2022 10:04 AM | |
Joined: 1/21/2013 Last visit: 9/26/2024 Posts: 3134 Rating: (489)
|
Hi crkz94, the S7 protocol is a proprietary protocol from Siemens. In most cases, you must expect many limitations when using it with third-party products. You will find according information in the Ignition manual. I would recommend you the usage of OPC UA. Kind regards |