Hello, I am using SIMATIC S7-1200 (CPU 1215C DC/DC/DC) and I want to interface a pt-100 sensor with it. Please, let me know which one will be compatible with it. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 04/29/2024 12:11:08New subject after splitting |
|
4/29/2024 6:52 AM | |||||
Joined: 3/11/2019 Last visit: 9/6/2024 Posts: 1569 Rating: (289) |
Hi, the CPU itself does not have analog inputs for direct use of PT100. So you will either need an external converter or a analog input module compatible with PT100. Information can be found in technical data. Some possible solutions were already posted above. For example: 6ES7231-5PF32-0XB0Input ranges (rated values), resistance thermometer