Hi, I'm using TIA PORTAl V11 5.1 SP2 and when i try use output of a timer (TON/TOF/TP), to activate the input of a counter, the counter don't work. I'm using S71200 1215C AC/DC/RLY. How can i do it works??? Thanks! ------------------------------------------------------------------------------------------ |
Last edited by: ManoloJr at: 3/14/2016 4:10:19 PMLast edited by: Min_Moderator at: 3/15/2016 1:17:22 PMNew subject after splitting Last edited by: ManoloJr at: 3/15/2016 2:18:35 PM |
|
3/24/2016 2:28 PM | |
Joined: 7/7/2010 Last visit: 11/6/2024 Posts: 15385 Rating: (2443)
|
On the output of the TON/TOF/TP, add a positive transition contact with the TON.Q tag for that timer to drive your counter. This will have the effect you want provided your timer reaches the preset.
|
science guy |
|