10/2/2012 5:00 PM | |
Joined: 9/27/2006 Last visit: 9/13/2025 Posts: 12407 Rating:
|
Hello manu; The tables you will find in the attachment are extracted from this manual, which you should keep with you if you are troubleshooting a S7-400H system: SIMATIC Fault-tolerant systems S7-400H At first glance you seem to have lost communcations redundancy at the level of a Profibus-DP/Profinet-IO slave . Open your diagnostic buffer to identify the failing station and check it out properly.If entries in the diagnostic buffer are not clear to you, you can save it ("As Text") and post it here on the forum as an attachment so we may look at it and help you do the diagnostics on your system. Hope this helps, Dniel Chartier |
Last edited by: dchartier at: 10/2/2012 6:43 PM |
|
This contribution was helpful to
1 thankful Users |
10/14/2012 12:27 AM | |
Joined: 9/27/2006 Last visit: 9/13/2025 Posts: 12407 Rating:
|
Hello sp88; |
This contribution was helpful to
4 thankful Users |