Hello mohamed; First, about your last ppoint: you remove the erro LEDs on you CPUs by correcting the faults that cause the LEDs to light up. You cannot remove or mask them any other way. - the BusXf LED appears when the operating system of the CPU detects an error on the network that links the CPU and the remote I/O stations (on Profibus or Profinet for example).A faulty node interface or module, connector of cable could be the source of the fault. - the REDF LED lights up when the operating system detects a redundancy fault between the primary and stand-by CPUs in a redundant system. This could be a problem with the sychronization modules or F.O. cables between the CPUs. To have better information on the source of your problems you should open the diagnostic buffer of the CPUs. This is a memory location where all diagnostic messages of the CPUs are maintaned and made available to the user. So open the diagnostic buffer on the primary CPU and start examining the messages there, study the messages that appear to relate to your LEDs in particular. If you need help understanding the diagnostic messages, there is a button on the diagnostic buffer screen that allows you to Save As a text file the complete list of messages currently in the buffer. You can attach this text file to your next post so we can study it and help you further. The screenshots below are taken from the S7-400H fault-tolerant system manual, which you should consult whenever you have problems with your redundant CPUs: https://support.industry.siemens.com/cs/ww/en/view/82478488 Hope this helps, Daniel Chartier |
1/8/2019 9:13 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello mohamed; Very often (some estimates go up to 85% of all Profibus failures) the problem in a Profibus network lays in the infrastructure, cable, connector, termination... This very useful article from Profinet.com is very informative on this subject: https://us.profinet.com/top-5-reasons-your-profibus-network-failed/ It also provides a link to the Profibus installation guidelines, from Profibus International. Follow the tips in the article to correct the problems in your installation and then study the guidelines for more familiarity. I presume from your question that your SCADA is also part of the Profibus network. If it is a Siemens software, then it acts as a Master (class 2) on the network and should not affect the other slave nodes present. You must simply make sure that it is cabled and terminated properly in the network. If it not a Siemens software, you must find out if it acts as master or slave on the network, and that the length/speed requirements over a segment is respected, and that each segment does not carry more than 31 nodes (plus a repeater, if necessary). Hope this helps, |
1/8/2019 9:24 PM | |
Joined: 1/12/2012 Last visit: 1/13/2025 Posts: 22 Rating:
|
My scada system connected to the plc through Ethernet not a profibus |
1/9/2019 9:11 AM | |
Joined: 1/12/2012 Last visit: 1/13/2025 Posts: 22 Rating:
|
Dear Eng.Daniel here attached our diagnosis for my problem. AttachmentDiagnose8.1.2019.txt (577 Downloads) |
Follow us on