Hi I got a connection between 2 Schneider PM1200 Power Meters and S7-1200 PLC through Modbus RTU.I read the current value of phase 1in the address registers 3929 and 2925of PM1200s.But I received variable and irrelevant values.What's wrong? I attached my project pictures and PM1200 manual. Best Regards. AttachmentUser Manual PM1XXX_EN.zip (1009 Downloads) |
9/13/2013 5:57 PM | |
Posts: 14 Rating:
|
Hi huggy_d1 Modbus register address instead of absolute register address. In this case add 40000 to the above address and use it. For example, VA parameter absolute address is 3901. Modbus address can be 43901 (40000+3901). [page 64] Attachments71200manual_Modbus_RTU.pdf (855 Downloads) |